a 50A breaker. 40 A max writtern on the receptale is to limit the current drawn from the breaker to its 80%.
To use PVC conduit was the electrician's word. Here they go by NEC 2017. I use Romax 6/3, it's indide a garage.
a 50A breaker. 40 A max writtern on the receptale is to limit the current drawn from the breaker to its 80%.
To use PVC conduit was the electrician's word. Here they go by NEC 2017. I use Romax 6/3, it's indide a garage.
•
室內是否可以不用conduit?室外是否一定要鐵管?我記不清了。
-chinomango-
♂
(0 bytes)
()
07/28/2023 postreply
14:49:28
•
Romax 在drywall 後不用conduit,室外該用啥沒關心
-MoonRiverMe-
♂
(0 bytes)
()
07/28/2023 postreply
16:34:24